OK, I understand a bit better what you are doing now.
First, to use the master/slave function of Cuecores it's better to have tracks that have been recorded together, I don't know if it's your case.
Now, the B-station template is using API commands to control the CueCores.
First you can check in the monitor page that the Cuecore 3 is receiving the OSC messages, if not hat means that there is a problem with the ip settings or network.
If the Cuecore 3 receives the OSC command, check that the first word in the osc message is the same than the API prefix of the Cuecore 3 ( see in the setting page)
/
core/pb/1/go+ ( core in this exemple).
If evrything is set right it should work.
If not send me an email at support"at"visualproductions"dot"nl, with your details and I will help you directly by phone.
Enjoy